OCCUPANCY SENSORS

Introduction: ASHRAE 90.1-2001 contains a number of mandatory control requirements. The Standard’s requirements for automatic shut-off and space control can be satisfied using occupancy sensors.

When occupancy in a given space is predictable, switching can often be scheduled using simple devices such as time-clocks and timer-switches to save energy. When occupancy is not predictable, then switching can be automated using occupancy sensors.

Occupancy sensors detect when a space is occupied or unoccupied and turn the lights on or off automatically after a short period of time to save energy.

Energy Savings: Depending on the characteristics of the space to be controlled, energy savings as high as 90% can be realized through use of occupancy sensors, according to the U.S. Environmental Protection Agency.

Occupancy area

Energy Savings

Private office

13-50%

Classroom

40-46%

Conference room

22-65%

Restrooms

30-90%

Corridors

30-80%

Storage areas

45-80%


In 1997, researchers studied energy savings potential for occupancy sensors in buildings in 24 states representing a cross-section of commercial building types*. The study monitored occupancy and the number of hours the lights were on in 158 rooms, including 37 private offices, 42 restrooms, 35 classrooms, 33 conference rooms and 11 break rooms. Potential energy savings for these spaces types were calculated as follows.

Space Type

Savings Potential All Hours

Savings Potential Normal Hours

Savings Potential After Hours

Restroom

60%

18%

42%

Conference room

50%

27%

23%

Private office

38%

25%

13%

Break room

29%

14%

15%

Classroom

55%

23%

35%

*Maniccia, D. et al, “An Analysis of the Energy and Cost Savings Potential of Occupancy Sensors for Commercial Lighting Systems,” Proceedings of the 2000 Annual Conference of the Illuminating Engineering Society of North America.

Sensor Variables: When specifying an occupancy sensor, the below variables are relevant.

Technology

Choose method of motion detection that will best meet the application need.

Sensitivity

Determine how sensitive the sensor should be to movement so that it effectively detects minor and major motion without nuisance switching (false-on/off). Sensors are now available which provide automatic adjustments of time delay and sensitivity. In these models, manual set-up and subsequent adjustments are unnecessary.

Coverage area

Specify range (ft.) and coverage area (sq.ft.) for the motion detector based on the desired level of sensitivity.

Mounting

Locate the sensor for maximum effect.

Time delay

Determine how long the sensor should wait before turning out the lights when the space is unoccupied to be convenient for users but also maximize energy savings. Sensors are now available which provide automatic adjustments of time delay and sensitivity. In these models, manual set-up and subsequent adjustments are unnecessary

Cut off

Determine whether the occupancy sensor’s coverage area must be restricted so that it will not monitor adjacent areas that should not be monitored (such as a hallway outside a controlled private office).

Special features

Specify special features for the sensor based on available offerings from manufacturer and application need.


Sensor Technologies:
Occupancy sensors detect the presence or absence of people using one or a combination of several methods. The most popular methods are passive infrared (PIR) and ultrasonic. Dual-technology sensors use both methods. Each method has advantages and disadvantages that make it more suitable for some applications than others.

PIR Occupancy Sensors: PIR occupancy sensors sense the difference in heat emitted by humans in motion from that of the background space. These sensors detect motion within a field of view that requires a line of sight; they cannot “see” through obstacles.

The sensor’s lens views its coverage area as a series of fan-shaped coverage zones, with small gaps in between, and is most sensitive to motion that occurs between each zone (lateral to the sensor). The farther one is from the sensor, the wider the gaps between these zones become, which decreases sensitivity proportional to distance and can result in nuisance switching (false-off). Most PIR sensors are sensitive to full body movement up to about 40 ft. but are sensitive to hand movement, which is more discrete, up to about 15 ft.

Ultrasonic Occupancy Sensors: Ultrasonic occupancy sensors utilize the Doppler principle to detect occupancy through emitting ultrasonic sound waves throughout a space, sense the frequency of the reflected waves, and interpret change in frequency as motion in the space. These sensors provide volumnmetric coverage and may not require a line of sight position as long as hey are not fully blocked by obstructions such as bookcases. partitions which extend to the floor, etc.

The sensor's transmission does not include gaps between discrete coverage zones making up the field of view and so can be sensitive to hand motion at distance up to 25 ft. However, the sensitivity of ultrasonic sensors makes them vulnerable to nuisance switching (false-on) due to confusing air movement near a supply grille, for example, with human motion.

Dual-Technology Occupancy Sensors: Dual technology sensors employ both PIR and ultrasonic technologies. They
activate the lights when both technologies or only the infrared technology detect the entrance of people. Lights are deactivated only when both technologies no longer detect the presence of people. This redundancy in method virtually eliminates the possibility of false-on and significantly reduces the possibility of false-off. Appropriate applications include classrooms and other spaces with low motion levels by occupants.

Another type of dual-technology sensor combines PIR technology with acoustic detection to reduce the possibility of nuisance switching.

Method

PIR

Ultrasonic

Coverage

Line of sight

Field of view can be adjusted by user

Covers entire space

Field of view cannot be adjusted by user

Detects hand movement

Up to 15 ft.

Up to 25 ft.

Detects arm and upper torso movement

Up to 20 ft.

Up to 30 ft.

Detects full body movement

Up to 40 ft.

Up to 50 ft.

Coverage area

300-1000 sq.ft.

275-2000 sq.ft.

Highest sensitivity

Motion lateral to the sensor

Motion to and from the sensor

Coverage Area: Manufacturers publish range (ft.) and coverage area (sq.ft.) for their sensors in their product literature. Many different coverage sizes and shapes are available for each sensor technology. The coverage area may show the maximum range and coverage area for minor motion (hand movement), medium motion (arm and upper torso movement), and major motion (full-body movement). The published pattern is often based on the maximum sensitivity setting for the sensor. Effective minor motion detection (motion at a desktop such a reaching for a telephone, turning a page in a notebook, etc., is critical to ensure that lights are not turned off inadvertently in occupied offices and classrooms.) The NEMA WD-7 Guide for Occupancy Sensors describes a robotic test for use
by manufacturers in determining and claiming minor motion coverage dimensions.

Mounting: Below are typical mounting configurations for occupancy sensors.

Mounting Configuration

Description

Ceiling

Appropriate for large areas that feature obstacles such as partitions, in addition to narrow spaces such as corridors and warehouse aisles. Units can be networked for control of areas that are larger than what can be controlled by a single sensor. Typically 2-3 times higher installed cost than wall switch sensors, but can be very economical if controlling large zones.

High wall and corner

Similarly appropriate for coverage of large areas that feature obstacles.

Wall switch (wall-box)

Appropriate for smaller, enclosed spaces such as private offices with clear line of sight between sensor and task area. Relatively inexpensive and easy to install.

Workstation

Appropriate for individual cubicles and workstations. The sensor is connected to a power strip for simultaneous control of lighting and plug-in loads such as computer monitors, task lights, radios and space heaters.



 

Mounting Location

Sensor Technology

Angle of Coverage

Typical Effective Range*

Optimum Mounting Height

Ceiling

US

360º

500-2000 sq.ft.

8-12 ft.

Ceiling

PIR

360º

300-1000 sq.ft.

8-30+ ft.

Ceiling

DT

360º

300-2000 sq.ft.

8-12 ft.

Wall switch

US

180º

275-300 sq.ft.

40-48 in.

Wall Switch

PIR

170-180º

300-1000 sq.ft.

40-48 in.

Corner wide view

PIR/DT

110-120º

To 40 ft.

8-15 ft.

Corner narrow view

PIR

12º

To 130 ft.

8-15 ft.

Corridor

US

360º

To 100 ft.

8-14 ft.

High mount

PIR

12-120º

To 100 ft.

To 30 ft.

High mount corner

DT

110-120º

500-1000 ft.

8-12 ft.

High mount ceiling

DT

360º

500-1000 ft.

8-12 ft.

*Sensitivity to minor motion may be substantially less than noted above, depending on environmental factors. See the NEMA WD-7 Guide to Occupancy Sensors which describes the robotic test recommended for determining minor motion coverage.

PIR = passive infrared, US = ultrasonic, DT = dual-technology

Adapted from 2001 Advanced Lighting Guidelines, New Buildings Institute.

Special Features: Depending on the manufacturer, a number of special features may be available for its products that can be used to optimize their application.

Manual-On Operation: The most specified control option for occupancy sensors is automatic-on—the sensor turns on the lights automatically when a person enters the space. Some sensors, however, are available with a switch and require a manual-on operation. This can increase energy savings because the occupant has the option to not turn on the lights because of available daylight or task lighting.

Masking Labels: PIR sensors may be available with masking labels that allow the coverage area to be fine-tuned to prevent false-on triggering. For example, if a sensor’s coverage monitors a private office but also an adjacent corridor, then the masking label can be used to obstruct the sensor’s line of sight to the corridor.


Bi-level Switching:
Bi-level switching is encouraged by most energy codes and is a requirement for qualifying for the Commercial Buildings Deduction. Some power-packs include two separate relays for controlling two circuits simultaneously or independently. This allows the sensor to integrate two manual switches for bi-level switching, which saves energy. For example, in a four-lamp troffer, one switch could control the ballast powering the outboard lamps, and the other switch could control the ballast powering the inboard lamps. Automatic, occupancy sensor wall switches which
can switch either or both of the loads are available.

Daylight Switching: Some sensors can work with a light sensor to turn off the lights in response to sufficient ambient daylight and/or prevent the lights from reactivating as long as sufficient daylight is available. The setting is typically adjustable and can be overridden. Caution: Ensure that the position of the
sensor which incorporates a photocell is placed where it will measure the foot candles on the work surface and that the photocell technology used is capable of measuring light levels accurately.

Combination Dimmer/Occupancy Sensor: Some wall-box sensors combine the functionality of an occupancy sensor and dimmer. The lights can be switched or dimmed based on occupancy. Dimming fluorescent and HID lighting requires a compatible dimmable ballast.

Isolated Relay: Some power-packs and/or sensors contain a separate small low-voltage switch for control of and interfacing with additional loads such as HVAC, security and building automation systems. For example, people entering a building after hours trigger not only the required lighting, but also heat or air conditioning as well.

Integration with Fixtures: Like photosensors, occupancy sensors may be available as an integrated component within a light fixture for easier installation and an integrated appearance.

see also:
Bi-Level Switching